Hello alanled; There was a very similar question a few days ago, you might find the ansers useful for you application, triggering PLC Job 51 with the activation of your input bit for example: /tf/WW/en/Posts/83476#top Hope this helps, Daniel Chartier |
11/26/2012 10:39 PM | |
Joined: 7/7/2010 Last visit: 2/14/2025 Posts: 15653 Rating:
|
The KTP400 is very limited. It requires the use of the area coordination to activate screen changes. The trigger on change option and cycle continuous option are not available with WinCC in TIA Portal V11 SP2 Update 5 (and all earlier portal versions as well). The information is available in the online help (press F1 while viewing the connections section of the HMI portion of the project). It describes what to do with the values. See the attached image for the area coordination tags needs to handle screen changing and knowing what screen is currently visible. I used a DB to make it easier for me to keep it all in one spot. AttachmentHMI_Area_Coordination.zip (155 Downloads) |
science guy |
|
This contribution was helpful to
1 thankful Users |
11/27/2012 2:40 PM | |
Posts: 11 Rating:
|
many thanks for this. |