Hi... Anyone tell me what is Active Field Distributor..? And when it is used... Also plz tell me the difference between PROFIBUS DP and PROFIBUS PA... |
1/21/2013 3:43 PM | |
Posts: 1 Rating:
|
In a mixed connection type (AFD's and AFDis) supports a ring redundancy connection?. Please answer, is urgent. Best Regards.
|
1/21/2013 4:16 PM | |
Joined: 9/27/2006 Last visit: 3/23/2025 Posts: 12344 Rating:
|
Hello alej; The attached extractwas taken from the following manual; itshould give you your answer: Ring redundancy is possible with a maximum of 5 active field distributors with mixed use of AFD and AFDis. SIMATIC Bus links DP/PA coupler, active field distributors, DP/PA Link and Y Link Hope this helps, Daniel Chartier |