4/22/2015 7:20 AM | |
Posts: 1299 Rating: (136)
|
Hello, which device and software version are you using? I already used this function with a comfort panel K!ke |
4/22/2015 3:28 PM | |
Posts: 116 Rating: (2) |
Hi, I work with TIA WinCC Advance V13 SP1 and TP1200 comfort panel. Regards, |
4/24/2015 11:57 AM | |
Posts: 1299 Rating: (136)
|
Hello, can you add some pictures of your project and the error? K!ke |
4/25/2015 3:10 AM | |
Posts: 116 Rating: (2) |
Hi K!Ke, Here is a detail. By the way, I'm looking for some detail about HMIRuntime structure where I can find detail for each parameter. I'm not sure which parameter I can read or write. Do you have any good reference for that? Thanks, AttachmentActivateIOField.zip (1014 Downloads) |
4/28/2015 1:22 PM | |
Posts: 1299 Rating: (136)
|
Hello, delete the "..= true" after .activate in your script.. Here you can find the information: https://support.industry.siemens.com/cs/ww/en/view/109091876/36126116107 K!ke |
This contribution was helpful to1 thankful Users |