1/28/2011 3:21 PM | |
Posts: 64 Rating: (0) |
On 02OCTt2010 somebody from our maintenance department has switched the power of from the PLC. A day later we noticed that all the configurable parameters that can be changed from the operating panel where changed. How is this possible with this CPU (315-2AG10-0AB0)that contains a MMC card? I thought that when there is a power loss on the CPU, the CPU makes a copy from the data blocks from the working memory to the load memory (MMC). When the power is back on, the CPU is copying the DB's back to the working memory (and other blocks) so the CPU is running with the same parameters as before the power loss....Is my thinking correct?
AttachmentDiagnostic buffer AUT-002 on 23dec2010.pdf (241 Downloads) |
1/28/2011 3:27 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Hello, Look at What is the effect of the STEP 7 function "Copy RAM to ROM"?
I think now is clear the situation. Best regards, Hristo Mihalev |
Last edited by: UMENCHO at: 1/28/2011 3:28 PM |
|
This contribution was helpful to1 thankful Users |
1/30/2011 12:45 AM | |
Joined: 10/7/2005 Last visit: 5/11/2024 Posts: 3005 Rating: (1047)
|
Hello KGI you are correct, DB's in S7 PLC's with MMC are generally retentive und you should not have "lost" their values. Nonetheless there are still a few things that can lead to a loss of DB values such as: 1.) Not enough memory left on the MMC to store the values of all retentive DB's 2.) DB's are created on PLC startup 3.) DB's are declared as non-retentive 4.) Someone did an overall reset of the CPU (which would shown be in your Diagnostics Buffer though and does not appear to be the case here) 5. ) Someone downlaoded the DB's (or whole program) after the power failure (which would NOT be shown in the Diagnostics Buffer) Below are a couple ofFAQ's which havemore info onthis: Retentivity behavior of S7-300 CPU 31x and complete devices C7-6xx with MMC How can you back up the actual values of DBs and bit memories? Last but not least, it is also conceivable that your HMI has a function or feature that overwrites the DB's after a power failure. I hope this helps and please let us know what you find |
Cheers |
|