9/28/2006 8:34 AM | |
Joined: 5/22/2006 Last visit: 4/16/2024 Posts: 7 Rating: (0) |
Hello You have to use SFB52/53 to read/write a data record from/to the sinamics and the address you have to use is the diagnostic address. The way you have to code the telegramm is described in the "PROFIdrive Profile Drive Technology". If you don't want to program this communication there is a product "Drive ES SIMATIC" which contains a block for acyclic communication with the drives. For more informations see the following link: http://www.siemens.com/drive-es |
9/28/2006 2:02 PM | |
Posts: 11 Rating: (1) |
Thanks, It's working now (once I figured out what the heck is "data set 47"). I'm using SFC 58/59 instead of SFB52/53. Bob |
1/23/2007 11:43 PM | |
Posts: 11 Rating: (1) |
"recnum" is record type number. You should use type 47 which is 2F Hex. So, your "recnum" = B#16#2F BobR |
1/24/2007 4:35 PM | |
Joined: 12/19/2006 Last visit: 3/13/2024 Posts: 22 Rating: (2) |
Thanks a lot, [;)] now it's finally working fine. Best regards, |
2/21/2007 7:49 AM | |
Joined: 5/12/2006 Last visit: 4/18/2024 Posts: 22209 Rating: (2979) |
hope this helps
AttachmentDPV1_Parameter_model.pdf (1070 Downloads) |