we lost the conection for the 3 simocode addres 3,4,19 !!!!!! i have no idea why maybe ther is somerhing with the order for those 3 that i didn't respect |
12/29/2015 6:33 AM | |
Joined: 5/12/2006 Last visit: 3/25/2025 Posts: 22600 Rating:
|
Hello, check the new PROFIBUS Cable and Connectors, and the termination on the connectors.
Christoph |
12/29/2015 10:49 AM | |
Posts: 101 Rating:
|
Problème Resolved the Profibus cable connected to 3 Simocode was poorly wired |