Joined: 9/27/2006 Last visit: 1/16/2025 Posts: 12329 Rating: (2699) |
Hello Anil; Your question could be understood in various ways, so here are a few answers: 1) How to setup the PA slaves with a DP/PA link and FDCs? You could start by looking at the following PAQ; although it mentions the IM-157 (designation of the old model of DP/PA link), what is said also applies to the IM 153-2: http://support.automation.siemens.com/WW/view/en/22729270 Read especially the second section, on using DP/PA links. 2) How to parametrize the individual PA slaves once connected to the Profibus network? This cannot be done through the Step 7 software; you need a special software calledSimaticPDM.to set the instruments up. (tag names, ranges, spans...). Step 7 will allow the PLC to read the actual values and a diagnostic byte for the instruments but not parametrize them. Manual: The Simatic Process Device Manager http://support.automation.siemens.com/WW/view/en/22729270 Manual: PDM v. 6.0 Getting Started http://support.automation.siemens.com/WW/view/en/21406135 |