Hi, It seems that you are not looking at the right card. If you have a card with SF and CPU doesn't have any fault at all, thatmeans that the card is not in the hardware config of the plc so plc doesn't detect it and doesn't communicate with it. 1. Check Hardware Config 2. Check the Physical Rack 3. Check the address 4. Download your hardware Config Regards, Behnam www.sigmaprocess.ca |