Hello all, I have a S7-313C with a CP343-1 Lean. I need to receive data from a datalogic BC9180 Base via ethernet. (other post about BC9180) I have the connection working but AG_RCV only receives data when the full length of the buffer has been received. if i put 100 bytes, only when the data received reaches 100 byte is transfered for the buffer. I read a code with 22 chars, i only receive after 5 readings (> 100 byte). Is this a known behaviour? Cheers, Luis Matos |
7/11/2019 2:29 PM | |
Posts: 3093 Rating:
|
Hello, Regards, |
7/11/2019 5:56 PM | |
Posts: 3093 Rating:
|
Section 4.4.1 in SIMATIC NET: S7-300/400 - Industrial Ethernet / PROFINET Configuring and commissioning S7-CPs for Industrial Ethernet |