Dear all, I am using IM 151 -8PN/DP CPU with analog input and output cards, Recently i added one more 2AI I 4-20mA module 6ES7 134-4GB01 -0AB0. I have two cases mentioned below 1. I connected 2 wire transmitter directly to first channel of AI module and i am able to read the siganl to plc. 2. I am using p & f Analog isolating barrier in between pressure transmitter and AI module for Ex proof reason. transmitter connected input side of Isolating barrier and AI module connected with output side of barrier. the barrier output is source type and my AI channel also generating 24volts for the field device, i think because of this reason i am not reading the siganl to PLC. I uploaded isolating barrier data sheet. please help to find some solution AttachmentKFD2-STC4-EX1.pdf (637 Downloads) |
4/7/2016 12:12 PM | |
Joined: 7/2/2008 Last visit: 3/19/2025 Posts: 928 Rating:
|
Hello dhinagaran.v, Unfortunately, the barrier you have has an active output. This will not fit for your 2-wire analog input module. You have two options. 1- Add a new 4-wire analog input module (e.g. 6ES7134-4GB11-0AB0). I think this will be lowest cost. 2- Replace the P+F barrier with one that has sink output (e.g. KCD2-STC-Ex1). You can find more configurable barriers other than P+F by some quick search(e.g. PR electronics).
Best regards,
H-H |
This contribution was helpful to
2 thankful Users |
4/9/2016 4:29 PM | |
Posts: 784 Rating:
|
Hello Experts, Kindly explain the following idea: Active O/P from the barrier (Source) connected to 4 wire analog I/P module(Sink) Sink O/P from the barrier connected to 2 wire transmitter module(Source) |
4/10/2016 2:25 PM | |
Joined: 7/2/2008 Last visit: 3/19/2025 Posts: 928 Rating:
|
Hello Wago, I thought it was clear. I hope you wouldn't get more confused by what follows. Basically, you should understand the possible connections and terms of normal applications where transmitters are connected directly to analog input modules. Active/source device (module) means that this device has a DC potential across its terminals. Passive/Sink means this device doesn't generate any voltage across its terminals. Two wire transmitter is a passive component (varies the mA in the loop according to measurement but needs DC voltage to operate). Two wire analog input module is an active module (has DC voltage across its terminals to supply 2-wire transmitters). 4-wire transmitter means it has separate two wires for power and and two wires for signals. The 4-wire transmitters will have (most likely) active 4-20mA. You can't have two active components in a single side of the loop. A two wire transmitter (passive) requires an active analog input module (2-wire analog input module). A 4-wire transmitter (active) requires a passive analog input module (4-wire analog input module). The barrier is a device that is used for transmitters in hazardous area (Ex barrier) or for higher isolation voltage (Isolator) between field and DCS/PLC. The barrier acts like an analog input module for the transmitter and acts like a transmitter for the PLC. Most of Ex barriers require external DC voltage to operate. Most of Ex barriers act as an active component for the AI module side. This means AI module should be passive (4-wire AI module). I hope it's more clear in the attached file. Regards, H-H Attachment2-wire & 4-wire connections.pdf (746 Downloads) |