Industry Online Support
Technical Forum
10/29/2010 3:28 AM | |
Joined: 10/7/2005 Last visit: 9/13/2024 Posts: 3020 Rating: (1054)
|
Hello erkanozdemir important thing to make sure first is to check that the measuring range module of the AI card is in the correct position("A" in your case and just in case you are not yet aware of this important range module). You'll get all the technical data, connection description,Analogue value representation etc. from the SIMATIC S7-300 S7-300 Module data manual (see chapter 4, 5& 6) and may also find the SM331; AI 8 x 12 Bit Getting Started part 3: Thermocouples guide helpful. I hope this helps and good luck |
Cheers |
|
Follow us on