1/23/2023 8:26 AM | |
Joined: 3/19/2012 Last visit: 11/27/2024 Posts: 6 Rating: (2) |
I do have the same issue only while controlling it with the "SinaSpeed" block. If I however open V-assistant and control the drive manually I can start and stop it without problem. Would someone have any idea how to fix this? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 01/23/2023 13:07:40New subject after splitting |
|
2/1/2023 12:42 PM | |
Joined: 12/16/2021 Last visit: 8/22/2023 Posts: 126 Rating: (2) |
Hi DonSebas, SINA_SPEED can be used if you just use the "normal" speed control inside the drive and you want to enable the axis and give a speed setpoint from PLC to the drive. So it is very simple block and you will need to use the standard telegram 1 1. Check back positive and negative speed limit - p2162 2. Check and correct the maximum speed (p1082). 3. Check and correct the speed limit (p29070, p29071), and the DI signals SLIM1 and SLIM2. Check back above points.
|
Last edited by: Jack0004 at: 02/01/2023 12:47:56If The Information Helpful, Then Don't Forget Give (To thank ) and Rate It |
|