11/18/2008 11:42 AM | |
Posts: 48 Rating: (0) |
can not see anything straightforward |
11/18/2008 5:25 PM | |
Joined: 9/27/2007 Last visit: 12/18/2020 Posts: 993 Rating: (102)
|
hi hv 77 Your discription is a little unstructured. IfI am wrong, tell me. - an alarm ist coming and you see the "c" blinking. - you acknowledge and the "c" is standig still - the alarm is going and you have to acknowledge again, to see the alarm not longer to solve that - open alarm logging - select the message class of the alarm - click in the menübar at "Edit" > "Properties" > "Acknowledgment" - deactivate "Acknowledgment Went Out" If that not solvethe problem, please describe the problem step by step. An alarm is triggert by rising or falling edge, so i think the problem isby WinCC projection. regards cumulus |