3/18/2013 7:05 AM | |
Posts: 6 Rating: (1) |
Hello! Dear specialists! I have project with PLC (CPU 313C-2DP) and HMI panel (TP900 comfort+ SD card 2GB) In project I make follows steps: In the "HMI alarms" editor 72 discrete alarms are created (fig.1) In the "Log" editor alarm log is created (fig.2) In the "HMI alarms" editor (Alarm classes) the error alarm class are configured (fig.3) In screen editor I added “alarm view” with next properties according to fig.4 Alarm screen works well when I use simulator! But in panel (TP900) alarm screen doesn’t work and has a system error (80052 Error during read access to log Alarm_log1) What isn’t correct in my activities? Best regards! Attachmentfigure1,2,3,4.zip (594 Downloads) |
3/19/2013 5:53 PM | |
Posts: 3037 Rating: (192)
|
Hello, You can find in the help of WinCC: 80052 Error: The log cannot be read. Check the log and the specified path.
|
3/19/2013 7:01 PM | |
Posts: 6 Rating: (1) |
Yes, sure I checked the log! And the log file is not created by the path of the SD card (Path \ Storage Card SD \ logs) |
3/20/2013 5:16 AM | |
Posts: 461 Rating: (29) |
|
4/12/2016 10:14 AM | |
Joined: 8/21/2014 Last visit: 9/19/2024 Posts: 1024 Rating: (14) |
New question published by Herbid68 is split to a separate thread with the subject Displaying alarm log in simulated HMI without PLC?. Best regards |
My Forum is the place to personalize your profile, |
|