1/17/2008 1:53 PM | |
Posts: 1776 Rating:
|
Hi, Alarm logging and Taglogging are working asynchronous. Wait is only active for TagLogging. So the sleep functions will be OK April |
1/21/2008 5:08 PM | |
Joined: 9/8/2005 Last visit: 9/11/2024 Posts: 177 Rating:
|
Hi, as far as I know the message trigger tag is reading every 500 ms from WinCC and the linked process value tags are read every 2 seconds only. So a sleep from min. 2 seconds are necessary. But sleeps in C scripts are very ugly. So my suggestion is to create the message manual. An example how to do this you will find in the FAQ: http://support.automation.siemens.com/WW/view/en/24325381 As message number you can choose the message number which shall created. Michel |