Good day to all! -- -- -- -- -- -- -- -- -- Windows 10 [Version 10.0.19045.2846] TIA V16 udp5 WinCC Adv V16 upd5 -- -- -- -- -- -- -- -- -- PLC: CPU 315-2 PN/DP V3.2 HMI: KTP700 Basic PN V16.0.0.0 -- -- -- -- -- -- -- -- -- When I start the HMI simulator and open a window that has an Alarm View, no alarms are shown in the window. At the same time, in the DB block, there are enabled bits for alarms. How can it be? HMI does not see enabled bits? This situation exists with the real HIMI. For some reason, Alarm_view sometimes doesn't display alarms for enabled message tags. As far as I understand, if the alarm tag is enabled, then the HMI should also show a message for it? Help please, how to solve this problem? -- -- -- -- -- -- -- -- -- alarm_view (reuploaded) alarm tag (reuploaded) alarm_view property (reuploaded) AttachmentFiles.zip (201 Downloads) |
Last edited by: ProgIga at: 04/14/2023 13:34:49Last edited by: Jen_Moderator at: 04/17/2023 04:42:11All files added as .zip file. |
|
4/14/2023 11:12 AM | |
Joined: 8/3/2009 Last visit: 4/17/2025 Posts: 15311 Rating:
|
Hello ProgIga Use an IO field and show the definied boolean or word in Rutnime , do you see also 1 and 0 in the IO field? acitvate all alarm classes in the alarm view, perhaps you have set this alarm in another alarm class. And if nothing works you can also try to clear the temporary data: https://support.industry.siemens.com/cs/de/en/view/109778709 Bye Murof |