Hello Sangito I haved worked with Program_Alarm and Comfort Panel with WinCC V7.X and TIa V13/14 with TP1200 Comfort. The only trap in which i tapped was, that if you have checked the Automatical Update in The Runtime Settings-> Alarms. then the PLC Alarms are not shown at HMI->Alarms-> PLC Alarms. They will be generated automatically in the Runtime. If you diasable them then you could create a List of the PLC Alarms. A good FAQ for Program_alarm is: https://support.industry.siemens.com/cs/ww/en/view/62121503 Bye Murof |