2/19/2008 3:10 PM | |
Posts: 1776 Rating: (95)
|
Hi, You don`t need to create Variables in alarm logging, you use the variables from the tag logging. Or what do you mean? |
2/21/2008 1:40 PM | |
Posts: 1776 Rating: (95)
|
Hi, have you seen this FAQ http://support.automation.siemens.com/WW/view/en/56558 |
2/22/2008 10:27 AM | |
Posts: 17 Rating: (1) |
Hi, I think that you need to use alarm_8p (SFB35) block. http://support.automation.siemens.com/WW/view/en/23730697 |
2/22/2008 11:37 AM | |
Posts: 28 Rating: (1) |
Hi, I think that could be the solution. Thank you very much sbc. |
Last edited by: jsanjose at: 22.02.2008 11:37 |
|
9/26/2008 4:21 PM | |
Posts: 8 Rating: (0) |
I think th easiest way is SFC17/18 SFC107/108 |
1/8/2009 3:27 PM | |
Posts: 261 Rating: (42) |
I am calling SFB35 in a standard FB. (see the attachment) In case of Alarm1 to 8 it works perfectly. But in case of Alarm9 to 16 in WinCC it shows the messages of 1 to 8. For Ex: For Alarm9 it show Run Feedback fault (class Alarm). Attachmentalarm.pdf (155 Downloads) |
This contribution was helpful to1 thankful Users |
1/12/2009 10:46 PM | |
Posts: 2661 Rating: (279)
|
Hi ddg, Check the values of EV_ID parameter. For each instance this parameter should be a uniquenumber. Normally it should get assigned automatically. Find attached an example SCL source file. Regards AttachmentALARM16.ZIP (153 Downloads) |