8/14/2014 6:58 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Could you please provide wiring diagram here? |
8/14/2014 10:31 PM | |
Posts: 9 Rating: (1) |
Hi Piscean 2010 I don't have access to the drawings as I suspect the contractor who installed this new card did so without updating or even using the existing drtawings. I've attached a very basic drawings of how the card has been installed. The 2nd group of outputs has been omitted for clarity and the only the first output has field wiring attached. The installation is an oilrig which means Neutral and Earth are the same. Hopefully this gives you some understanding of the situation. Regards Dan. AttachmentD:\tmp\upload\6ES7322-1FH00-0AA0.pdf (116 Downloads) |
Last edited by: CS Moderator at: 8/15/2014 3:10 PMAttachment reattached |
|
8/15/2014 5:35 AM | |
Posts: 1064 Rating: (72) |
If you disconnect the load on the card but leave the power connected do you still have all your outputs on(supplying voltage)? |
8/19/2014 8:57 PM | |
Posts: 9 Rating: (1) |
Hello Marko Today I rechecked my fault-finding and the output card will turn on the load when it is connected to the contactor coil. Dan.
|