3/23/2019 3:06 PM | |
Joined: 12/18/2014 Last visit: 6/14/2025 Posts: 35515 Rating:
|
In attachment a possible solution. Since you did not write, whether you have the PT100 on an AM2 RTD module or an external transmitter, I decided for an external transmitter with a 0-10V output. You also did not write anything about the measuring range, so I chose the range 0-100 °C. But you can change it. If you can not make it alone, then post. AttachmentAnalog_output_depending_on_the_temperature_0BA8.Standard.zip (363 Downloads) |
This contribution was helpful to
1 thankful Users |
3/23/2019 3:38 PM | |
Joined: 12/18/2014 Last visit: 6/14/2025 Posts: 35515 Rating:
|
The AM2 RTD has a fixed measuring range. The range goes from -50 to 200 °C. I have adapted the analog amplifier and changed the AI1 in AI 5. AttachmentAnalog_output_depending_on_the_temperature_V2_0BA8.Standard.zip (341 Downloads) |
This contribution was helpful to
1 thankful Users |
3/23/2019 4:09 PM | |
Joined: 12/18/2014 Last visit: 6/14/2025 Posts: 35515 Rating:
|
Hello AutoGen_911641, you're welcome... |
Follow us on