11/11/2010 12:01 AM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308)
|
Hello olloy, The 1KF01 means you either have a 4-wire transmitter or you have a 2-wire transmitter connected to a power supply as in page 299 (CH5 2DMU)in S7-300 module data manual. The -32768 means an underflow. In other words it means a valueof 0 mA which means no current (Maybe no power supply) or maybe a reverse current. I would suggest to check that transmitter is powered (working). If power supply is healthy and transmitter is working then add an ammeter in series to measure the current value (Double check current direction in circuit). Best regards. H-H |
11/11/2010 9:29 AM | |
Joined: 4/24/2008 Last visit: 8/2/2024 Posts: 213 Rating: (16) |
Have also a look to this FAQs. I think they will help you. http://support.automation.siemens.com/WW/view/en/22894127 http://support.automation.siemens.com/WW/view/en/22897109 |
|
|