I use analog input moduleAI8x13Bit (6ES7 331-1KF02-0AB0). I set the input to 4-20mA. What is the range I read in the PIW? Is it 0-32767?
|
12/29/2014 11:50 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
|
Hello, 0 to 27648, see SIMATIC S7-300 S7-300 Module data, chapter 5.1, Table 5-9 Regards, Marcjan |