9/2/2020 2:54 PM | |
Joined: 12/18/2014 Last visit: 12/4/2024 Posts: 34338 Rating: (4278)
|
Short and sweet: No.
|
This contribution was helpful to1 thankful Users |
9/2/2020 3:45 PM | |
Joined: 2/22/2008 Last visit: 11/18/2024 Posts: 2698 Rating: (208) |
If you allow other hardware options than Siemens Logo, then you can use a remote Modbus TCP/IP device, but you at least need a Logo 8.1 (FS4) or a brandnew Logo 8.2 for Modbus. Higher resolution causes a higher price, that's normal and you must think about the Logo arithmetic only calculates with integer values. Search for Adam-6717 on Advantech for example. Maybe you get lower price Modbus remote devices from China, but be careful, you need Modbus TCP/IP, not Modbus RTU. Lower prices often causes instability in 24/7 mode. For a little more money you can get a S7-1200 controller with high resolution analog inputs and a greater program memory. Regards, Scorp |
This contribution was helpful to1 thankful Users |