6/13/2022 11:27 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051)
|
hi Eliannya, I don´t know what you are doing, but the analog input representation that you show with your graphs are not matching the values as they should be according the manual: Measurement ranges of the analog inputs for voltage and current (SB and SM) obviously you are measuring the 0..5V on the module with a range of 0-10V, right? Try to use the measuring range of 0..5V or +/- 5V. Also use the rigth datatype on the input word. they should be integer, not unsigned integer or word. the jump from 65535 to zero is on the edge of a word. 16 bits can only represent values from 0 to 65535. But without further information I can´t say what is going wrong here. Please share information about the parameters of the module and how you process ist values. hope this helps, regards, |
Last edited by: mopS04 at: 06/13/2022 11:36:09FCK WAR! |
|