Hello, From the technical data here: http://support.automation.siemens.com/WW/view/en/6771964/td You will see that no range allows to read a esistance of 10 kOhm. |
Best regards |
5/5/2013 10:16 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
Hello, Set your module to 0-10V. Put a resistor of 10 K in series with the potmeter, +24V at the resistor, 0V at other end of potmeter, slider to analog input. Change the upperlimit to 27648. You will find a drawing of the potmeter connection here:/tf/WW/en/Posts/90890#top Regards, Marcjan