11/1/2010 8:32 PM | |
Posts: 21 Rating: (0) |
hi what is the normal voltage drop on a analog output (current mode 4-20 ma).is it fixed or variable because of current change? |
11/2/2010 8:28 AM | |
Joined: 10/7/2005 Last visit: 5/23/2024 Posts: 3007 Rating: (1049)
|
Hello nimalak not too sure ifI understand your question correctly, but I'll have a stab at explaining whatI think it is anyhow: A current Analogue Output (e.g. 4-20mA) will make sure to "drive"the requestedcurrent through the output. Example: Your Analogue device has a total "burden" resistance of 200 Ohm's (incl. cabling, terminal strips resistance etc.). You use a 4-20 mA Output and set the Analogue Output to 50%. The card will now "drive" 12mA through theloopfor which you will measure 2.4 V at the Analogue Output (200 Ohms * 12mA = 2.4V). If your burden resistance changes (e.g. bad connections), the Analogue Output will maintain the 12mA current by changing the Voltage at the Output (this is a big advantge of current AI's and AQ's over voltage AI's and AQ's). It can however only do so up to a maximal permissible overall burden resistance (typically 500 Ohms for an AQ, these values can be found in the product manual e.g. SIMATIC S7-300 S7-300 Module data.Note too max. open circuitOutput voltage of the AQ which typciallynot exceeds 18V). I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
11/2/2010 10:03 AM | |
Posts: 1 Rating: (0) |
Hi, It seems really helpful. RB
|