6/16/2020 11:27 AM | |
Joined: 3/30/2020 Last visit: 9/20/2024 Posts: 4777 Rating: (981) |
Hello. You can find the S7-1200 manual here: The partial connection diagram is: So I assume you need X11/2M to COM and X11/0 to AI3. Note that the analog output regulate between 0mA and 20mA. That means you will not use the range 0mA to 4mA. Have a look at the functions NORM_X and SCALE_X as described in the manual or in-software help. The number ranges are mentioned in the manual. |
Last edited by: qwazee at: 06/16/2020 11:28:23Activities of this user is voluntary. There is no obligation or liability placed on this user. Though optional, your 'please' and 'thank you' is highly valued. |
|
This contribution was helpful to1 thankful Users |
6/16/2020 12:31 PM | |
Posts: 12 Rating: (0) |
Thanks for the help! It really was how i thaught, I believed it was way too simple. I guess not. |
This contribution was helpful to1 thankful Users |