Dear vickyrocky, If you wrote in VAT, PQW300 for instance, you will not able to monitor this value. You can move it to memory area and then monitor it. To avoid this method, you can go to HW config, change the addresses of analog outputs to be inside the process image of the CPU. For example; PQW 300 became PQW 30.and then go back to VAT and write QW30 Note I have eleminated here the letter "P" Then you will be able to monitor it! Regards |