11/7/2009 11:02 PM | |
Joined: 9/28/2005 Last visit: 3/14/2022 Posts: 2957 Rating:
|
Hello, 4mA = 0 (dec) = W#16#0000 (hex) 20mA = 27648 (dec) = W#16#6C00 (hex) |
Best regards, |
|
11/9/2009 2:31 AM | |
Posts: 382 Rating:
|
Hi, Apart from Darius input, maybe this attach could give you a good reference too! with regards, how come AttachmentSimatic Analog Input Or Ouput Range.pdf (319 Downloads) |
11/9/2009 3:01 PM | |
Posts: 32 Rating:
|
Thank you all very much |
11/9/2009 3:59 PM | |
Joined: 5/28/2008 Last visit: 5/12/2022 Posts: 4362 Rating:
|
Dear LostPatrol, I think the following thread have a useful info for you. /tf/WW/en/Posts/26057 Regards, |
Ayman Elotaify |
|
11/11/2009 5:16 AM | |
Posts: 382 Rating:
|
Hi Cpt_KirK, I am not sure I can understand your question. Let me try to explain, 1] you can use FC106 in your step7 for analog output of 4-20mA. 2] in FC106 the "IN" value is the value that you input to give the result of 4-20mA output. 3] in FC106 the "HI_LIM" is the upper range valueand "LO_LIM" is the lower range values 4] in FC106 the "Bipolor" to be simple is the positive or negative range setting [see attach for better explaination]
5] if you set "HI_LIM" to 40.0 and"LO_LIM" to 0.0, once the "IN" value is 40.0, the "OUT" for example PQW320 will give you 27648 when you monitor from VAT table. At this time if you measure your AO card output with your meter, you will get 20.00mA. I hope this is what you are looking for. with regards, how come AttachmentUnscaling Values_ FC106_.pdf (154 Downloads) |
Last edited by: how come at: 11/11/2009 5:22 AM |
|