Hello IXO65, can you see the attached image? Because I can't see it on my cell phone. The problem is that the arithmetic instruction has to take P1 from an analog amplifier and it doesn't, but the analog output of the instruction seen in the online test is well calculated while Aq in the parameter list is zero. The question is, what can I be doing wrong? In the simulation it works perfect, but in the real device it does not work. Could it be a firmware error? Firmware version 1.82.01 Now I attach diagram, but I insist that it works well in the simulation. Thanks. AttachmentParameter_problem.lsc.zip (201 Downloads) |
7/30/2021 4:10 PM | |
Joined: 12/18/2014 Last visit: 1/13/2025 Posts: 34486 Rating: (4304)
|
You can update your firmware to the last version V1.82.04. First update to V1.82.02 and after that then to V1.82.04. Product information on the firmware update for LOGO! 8 for security Vulnerability CVE-2020-7593 |
7/31/2021 4:48 AM | |
Joined: 12/18/2014 Last visit: 1/13/2025 Posts: 34486 Rating: (4304)
|
Your firmware (V1.82.01) is the first version of the firmware for LOGO! 8.2. Then came the update to firmware V1.82.02 together with the update from LSC to LSC V8.2 SP1 (LSC V8.2.1). Information and Content LOGO! Soft Comfort V8.2 SP1 |