2/22/2017 11:44 AM | |
Posts: 88 Rating: (4) |
Dear experts, Analog output from sinamics control unit 240 E from pin 12(AO +) and 13(GND).Is it 2 wire or 4 wire. Regards |
2/22/2017 12:40 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
It is 2 wire type. Out put selectable either voltage 0-10 V or current 0-20mA. |
2/23/2017 7:17 AM | |
Posts: 88 Rating: (4) |
Yes, for taking current.The analog input card used is 6ES7134-6GD00-0BA1.The attached image consists of wiring diagram of the module. |
2/23/2017 8:04 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please set AO0 as voltage out put 0-10 V user need to set P0776 = 1. Connect 500 ohm resistor across it which will act as shunt & connect shunt feedback to PLC AI. Please refer the attached sheet for scaling information of AO. HTH. AttachmentCU240E AO setting.pdf (167 Downloads) |
Last edited by: PISCEAN 2010 at: 2/23/2017 8:09:02 AM |
|
2/23/2017 9:20 AM | |
Posts: 88 Rating: (4) |
by four wire ,is it possible to configure with the above method |
2/23/2017 9:55 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Do you mean to say at drive terminal end? No. |
2/23/2017 10:03 AM | |
Posts: 88 Rating: (4) |
so at analog input card of plc also it should be wired with 2 wire configuration,am i right? |
2/23/2017 10:12 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Yes, provided PLC analog input card must be compatible for 2 wire system. |
2/23/2017 10:18 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please study the attached folder in detail.
AttachmentCU240E terimnal details.zip (104 Downloads) |
2/23/2017 11:56 AM | |
Posts: 88 Rating: (4) |
what about wiring method using with attached file |
2/23/2017 1:00 PM | |
Posts: 88 Rating: (4) |
pin 26 and pin 27 AO also can be used .thats what I refered before in my post. |
2/23/2017 1:08 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Which post? |
2/23/2017 1:58 PM | |
Posts: 88 Rating: (4) |
in the picture which i attached before |
2/24/2017 7:24 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Yes. |
3/14/2017 8:42 AM | |
Posts: 88 Rating: (4) |
Thanks kbv.It is 4 wire system on plc side.We succeeded by four wire system |