Hello, Have a look into this manual: http://support.automation.siemens.com/WW/view/en/8859629 page 464 and 465. Terminals 21 and 40 are unused, so no extra power needed on these terminals. You will see that, if the board inputsare configured for Voltage output, the 4 last channels have a kind of read back inputs (S+, S-). These signals must be wired in that case, else the card overcompensate thinking there is an open loop). How are the channels configured? |