11/28/2016 4:29 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
Here is a possible solution.
AttachmentFill_level.zip (415 Downloads) |
This contribution was helpful to1 thankful Users |
11/28/2016 5:08 PM | |
Posts: 200 Rating: (6) |
Hi Thanks for the quick reply. this is what i had but not the scaling block. what is this used for. AttachmentAI TEST.pdf (346 Downloads) |
11/29/2016 9:57 AM | |
Posts: 200 Rating: (6) |
hi i have attached the manual for the float page 4 is the one we are using. VEGASON S 61 Attachmentvega-line-PriceList_GB.zip (352 Downloads) |
11/29/2016 1:25 PM | |
Posts: 200 Rating: (6) |
liquid |
11/29/2016 2:02 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
What is the maximum fill level of the tank? This limit can be parameterized at the sensor. And after the set value, the parameterization is carried out in the logo program. Attachment32944-EN-VEGASON-S-61.pdf (362 Downloads) |
11/29/2016 3:40 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
Here is a solution. The distance is scaled to 3.75m because the sensor must have a minimum distance to the medium of 0.25m. The analog input number depends on whether you use an analog input module and how many analog inputs are enabled on the basic module. AttachmentFill_level_V2.zip (260 Downloads) |
This contribution was helpful to1 thankful Users |
12/8/2016 3:07 PM | |
Posts: 200 Rating: (6) |
Hi i have the 2 AIs on the base ticked and then used AI3 the sensor i have been sent has a 2 wire output |
1/4/2017 3:13 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
At a maximum tank height of 2.30 m, a further 0.25 m has to be deducted because the minimum distance from the sensor to the medium is 0.25 m. In attachment the version adapted to your requirements. AttachmentFill_level_V3.zip (236 Downloads) |
This contribution was helpful to1 thankful Users |
1/4/2017 4:28 PM | |
Posts: 200 Rating: (6) |
Hi Thanks for the quick reply. i have added my program i cant seem to get the new settings right wounder if you could glance over it thanks Attachmentfill sensor.zip (267 Downloads) |
1/4/2017 4:48 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
In B034 you use the wrong operator1. Do not add, but multiply. |
1/4/2017 5:16 PM | |
Posts: 200 Rating: (6) |
i changed this setting well spotted but when i transfer to my logo it does not seem to work correctly as it does in the simulation |
1/4/2017 5:44 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
Since you do not write exactly what is in the LOGO! not working, I can only guess. Since I have no FS04, I can only check the program with my 0BA8.Standard. I have now made the necessary changes in your program. This included adjusting the bar graph in message text B031. In my LOGO! It works as desired. AttachmentPUMP V3 FB AI.zip (210 Downloads) |
1/4/2017 6:24 PM | |
Posts: 200 Rating: (6) |
hi i have converted to the standard logo AttachmentPUMP V3 FB AI (1).zip (249 Downloads) |
1/4/2017 6:42 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
The file V4 evaluates the signal from the sensor as a distance and converts it to filling level. Try it with this version. AttachmentPUMP V3 FB AI_V4.zip (230 Downloads) |
1/4/2017 7:36 PM | |
Posts: 200 Rating: (6) |
when i use the version 4 one it works that when i get closer to the sensor as in tank filling up the numbers and graph go down in numbers rather than in up |
1/4/2017 9:17 PM | |
Posts: 200 Rating: (6) |
Hi I do apologize for the grammar i did not understand that you came from Germany. I have attached a copy of the version that works best. I have the sensor on the bench in the workshop. i have measured a distance from the sensor 2m300 to a object to simulate the bottom of the tank. From this measurement i have marked the following. low-Low Low High High-High For example i have the Low at 1320 and this is what it reads on the screen. What i dont understand is that if the tank is 2m300 why at this level does it not read for example 500mm off the bottom of the tank. hope this helps Attachmentv4.zip (302 Downloads) |
1/10/2017 9:31 PM | |
Posts: 200 Rating: (6) |
Alls gone well with the project few tweaks here and there but all good. Thanks |
This contribution was helpful to1 thankful Users |
1/10/2017 9:42 PM | |
Joined: 12/18/2014 Last visit: 9/20/2024 Posts: 33807 Rating: (4200)
|
That is very nice. I am glad for you that it works. |
Follow us on