4/21/2016 4:56 PM | |
Joined: 7/18/2011 Last visit: 10/9/2023 Posts: 521 Rating: (91) |
Hi I think you will need to replace the CP521 by an S7- CP340 module Kind regards, BV |
4/21/2016 7:59 PM | |
Joined: 4/5/2006 Last visit: 8/13/2023 Posts: 642 Rating: (131) |
Hello, you can add a 6ES5 521-8Mxxx in S7 hardware configuration. Then i think it is possible to use it. RegardsAndré Räppel --------------------------------------------------------------------------------- www.raeppel.de
work faster with innovative PLC-Tools |
4/21/2016 8:17 PM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308)
|
Hello
CP340 cannot be installed in a ET200U Rack. You will have to Install it in the CPU rack or a separate ET200M Rack. |
Last edited by: Navnag at: 4/21/2016 8:25:33 PMThere is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
4/22/2016 5:19 AM | |
Joined: 3/2/2012 Last visit: 5/21/2024 Posts: 45 Rating: (0) |
thank you all, I will have a look in to the document... |