3/18/2020 3:27 PM | |
Joined: 2/1/2010 Last visit: 5/1/2024 Posts: 134 Rating: (68) |
Did you create all the s7 attributes on your custom block type for all the used IOs? I suppose you did, but just checking. If you run APDiag do you get any error messages when opening the faceplate? |
If my post helped you, please rate. Thanks. |
|
3/18/2020 3:38 PM | |
Joined: 5/3/2017 Last visit: 4/19/2024 Posts: 673 Rating: (216) |
Hi AutoGen_1260505, you didn't connect a variable to "LinkTag3", so you didn't have the permission to operate. Normally you connect the variable OS_PermLog to "LinkTag3" and with "BitIndex4" you define the Bit which has to be TRUE that you can operated. Helpful to create your own faceplates is the manual PCS 7 APL Style Guide, there you can find the description for the most attributes like "LinkTag3" and "BitIndex4" With regards |
3/18/2020 3:52 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
Hi, What value did you set under LinkedOp->LinkOp? It should also be ".Param_Force_Value". If not set, you won't get the permission. |
Last edited by: Oreca at: 03/18/2020 15:53:12If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
3/18/2020 4:06 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
Oreca, LinkOP and LinkedOP are the same variables. I try to parametrize link tag3, no results. Thanks. |
3/18/2020 4:37 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
In your last picture is another variable configured. Can you show me the complete setup of Links and LinkedOp |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 4:43 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
Yes, here. |
3/18/2020 5:38 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
Please change the value under: "OperationLevel". You forgot to add the point. Is this variable valid? Or does it need to be changed to: .Param_Force_Value#Op_Level? |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 5:44 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
Yes, i change it. I forget the ".". It doesn't work. |
3/18/2020 5:50 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
OK, are you sure you have the correct permission. Is this a custom block (SCL?). If so, please note the byteswap when the variables are sent to the OS. For example: In the OS_Perm, bit0 of the SCL block corresponds on the OS with bit 24. So please make sure to check the byteswap. Also check if you have configured the correct attributes. Structure values need S7_m_c and S7_xm_c. Also when using the #Op_Level, make sure attribute: Op_Level is correctly set. Which value is it? If the value is too high, the system does not recognize it. Also try to remove the tag at OperationLevel and use static 1, if the tag is still analogique.OosAct#Op_Level. I think a problem occurs because now you use a value inside a struct with the attribute Op_Level, but Op_Level must be used on the structure itself and not the value inside the structure. |
Last edited by: Oreca at: 03/18/2020 17:56:56Last edited by: Oreca at: 03/18/2020 17:58:56If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 6:14 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
I try with operationlevel variable, i change it with a internal variable. You can see with this screen. |
3/18/2020 6:15 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
I forget a new pics. Sorry |
3/18/2020 6:27 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
Hi, Remove the .Status1 completely and leave it blank. Status1 does not work. Post back the result please |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 6:33 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
Here is. |
3/18/2020 6:45 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
OK, then there must be something wrong with the OS_PermLog. Remove the .OS_PermLog and leave the value at -1, and set the BitIndex4 to 0. then try again. |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 6:51 PM | |
Joined: 11/7/2019 Last visit: 4/26/2024 Posts: 17 Rating: (0) |
NO changes |
3/18/2020 7:05 PM | |
Joined: 3/14/2008 Last visit: 4/26/2024 Posts: 2066 Rating: (928)
|
OK, Can you give me the system attributes that are set for tag: Param_Force_Value. A screenshot should be fine. The function also does not work when that value is not compiled properly due the missing attributes. Does the rest of the tags work in the faceplate? Did you change something in the Miscellaneous section under attributes: VersionID or TypeID? If so, change back because problems could occur in the scripts. You may also copy the APL_ANALOG_OP_DISPLAY from the @PG_PidConL_STANDARD and change the tags. If nothing works, send me the block and faceplate files so I can fix this (if you want). |
If I could help you, you can use the RATE button. Thank you. |
|
3/18/2020 7:06 PM | |
Joined: 2/1/2010 Last visit: 5/1/2024 Posts: 134 Rating: (68) |
We just finished a large project with many customized faceplates. A VERY stripped out application is attached, with limited functionality. Have a try at the values shown, those work. If not, I again suggest you check the APDiag output if you have wrongly configured tags. |
If my post helped you, please rate. Thanks. |
|
This contribution was helpful to1 thankful Users |