7/3/2017 3:55 PM | |
Joined: 3/14/2008 Last visit: 9/12/2024 Posts: 2095 Rating: (936)
|
Hi, I found your problem! But, its not due the system... In your SCL code variables OS_Start and OS_Stop are declared, but in the faceplate (@PG_OPTEST_Standard.pdl), you used OP_Start and OP_Stop. You used "P" instead of "S" After changing this in the faceplate, the OP button works, see attachment. You were on the right track! |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
7/3/2017 7:32 PM | |
Joined: 3/14/2008 Last visit: 9/12/2024 Posts: 2095 Rating: (936)
|
Hi Dave, Good that your problem is solved! And you are not the only one to make these mistakes Well, the upper and lowercase does not matter in tag management, but it does in script execution. And as your case points out, it does matter in the tags you call in objects as well. |
If I could help you, you can use the RATE button. Thank you. |
|
Follow us on