12/16/2011 1:43 PM | |
Posts: 3 Rating:
Hi Guys. Can someone please help me with this problem " Area error when writing ". How do i solve this problem? I have AttachmentDiagnostic buffer.zip (65 Downloads) |
12/19/2011 8:46 AM | |
Joined: 10/7/2005 Last visit: 6/9/2023 Posts: 2969 Rating:
Hello andrego can you afford to put your CPU into Stop? If so, delete OB121 from the PLC, it will then go into Stop due to the access error, "Open Block" will be available and take you straight to the isntrcution that causes the problem. I hope this helps |
Cheers |
12/19/2011 12:06 PM | |
Hello andrego it must work and as I'm not too sure what you have done, please try the following: 1.) Make sure OB121 has been deleted online from the CPU while the CPU is still in run (if you manually stopped the CPU to delete OB121, restart it to let it "crash" again). 2.)Your CPU must now "crash" due to the access error and the missing OB121 3.) Open the CPU diagnostic buffer. The last entry will simply tell you that the CPU is in Stop mode,the entry before that should contain the FC or FB that caused the access problem. 4.) Highlight it and you should have the "open Block" available. Please check this again and - should it still not work - let us know which of the above Steps did not work and post your CPU diag buffer here. I hope this helps |
Cheers |