Dear Michael, I am sorry but this sounds rather like a case dedicated for a Support Request. Please contact the international Customer Support by the use of the link on the top right side of this page, called Support Request. I am certain they may provide you more information. If you check the manaul: System Manual AS-Interface (Edition 11/2008) with Supplements (Edition 09/2010 - for displaying and configuring see Entry ID 44365425 ) you will find at page 174 the following fault inforamtion: Sensor supply overload (Slave is in RESET mode and switches off completely) to solve this the following is recommended: Unplug the sensor cables from the input sockets, user sensors with a lower overall current consumption, check the sensors/cables. Best regards J_Bell |
Last edited by: J_Bell at: 12/2/2010 4:39 PMManual added. |
|
12/3/2010 3:06 AM | |
Joined: 11/30/2007 Last visit: 1/6/2025 Posts: 59 Rating:
|
https://support.automation.siemens.com/WW/llisapi.dll?query=3RK2400-1FE00-0AA2&func=cslib.cssearch&content=adsearch%2Fadsearch.aspx&lang=en&siteid=cseus&objaction=cssearch&searchinprim=&nodeid4=20208582&x=23&y=9 This page should bring up information about your device. Sending the file for the indicators too. Attachment333045130DS03.pdf (84 Downloads) |