6/26/2014 4:06 PM | |
Posts: 1 Rating:
|
Hello everyone I have a ATV 31 and a siemens plc works with step 7 and I want to know how to connect the atv31 to the siemens plc in rs232. Thanks. |
6/26/2014 5:20 PM | |||
Joined: 9/27/2006 Last visit: 4/19/2025 Posts: 12346 Rating:
|
Hello juju; The ATV series of drives is developped by Schneider, and they all are Modbus slaves natively.To my knowlkedge they generally support RS-485, please make sure that your ATV 31 has a RS-232 communication port. as the following information would have top be slightly modified. Here is a link to Schneider documentation on Modbus communications to an ATV 31: ATV31 Modbus manual - Documents & Downloads So you would need a RS-232 Modbus master in the S7 system. One option that can be mounted in the main rack of a S7-300, or as part of a Profibus-DP remote IO ET 200M, would be a CP 341, with a Modbus master loadable driver (with physical dongle):
There are other options of course, depending on the S7 system you are using.If you have a ET 200S CPU (IM 151-7 for example) you could usew a serial CP 1SI as Modbus master, which would be a much cheaper solution (no loadable driver to purchase). Hope this helps, Daniel Chartier |
||