Hi dan.v. You could capture and record a change of the tag value in Audit Trail. Please refer to page 15 in the PDF documentation in above link: GMP-compliant Configuration with WinCC Comfort/Advanced, WinCC Audit and HMI-Panels https://support.industry.siemens.com/cs/ww/en/view/109744244 Best Regards, cga81 |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
1 thankful Users |
11/12/2020 8:56 AM | |
Joined: 7/1/2014 Last visit: 4/17/2025 Posts: 236 Rating:
|
First, thank you for the answer. Probably I was misunderstood. I already did waht is described on page 15. I assigned a PLC tag to the HMI and selected GMP relevant. The point is, if this tag is for example an Analog Input from the PLC, that changes his value constantly (or lets assume also with a PLC logic I just update it every 5 seconds), the AUDIT doesnt see this change, so it doesnt record the value changing. For what i see, tha only changes that are recorded, are actual operations on the panels, so for example a new SET on a value made on the panel, the touch of a button, the login, etc... I know the AUDIT probably is meant not for recording data like a DATA LOG, but the customer asked if it was possible to use it also for this purpose, so he had certified registration of DATA TRENDS.
|