12/9/2020 5:12 AM | |
Joined: 1/31/2020 Last visit: 1/8/2022 Posts: 3 Rating: (0) |
Hello Sir, Can you please help me to solve the encoder fault F31117 in CU250S2-PN, G120 drive. I am using Simotics M-1PH1 motor which has TTL encoder. Wiring is correct as per color code. I have connected encoder to D-Sub interface. Please suggest to rectify this problem. Thanks, Ram.
------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 12/09/2020 15:47:30New subject after splitting |
|
12/9/2020 5:13 PM | |
Joined: 7/7/2010 Last visit: 4/26/2024 Posts: 14639 Rating: (2349) |
Are you 100% sure the encoder signal is A & A- (like +5 & -5V), B & B-, and Z & Z-? Have you put an oscilloscope on the encoder signal wires to verify they are both above and below 0V reference for each channel and that A & B channels are able to indicate direction, and that the Z channel fires only once per revolution?
|
science guy |
|
This contribution was helpful to1 thankful Users |