10/1/2014 4:29 PM | |
Posts: 87 Rating: (7) |
Hi Ali Alkarn. This parameter it is available only for Smart Line Module (SLM) and Active Line Module (ALM). But you can check this document in the attachment file. Hope this helps. Regards
AttachmentVisio-fp_8760_01_eng.pdf (136 Downloads) |
This contribution was helpful to1 thankful Users |
10/2/2014 8:37 AM | |
Joined: 4/3/2014 Last visit: 9/9/2022 Posts: 54 Rating: (0) |
Hello againA.Gabardo, Thanks for the answer it was helpfull, but does this mean that the basic line module will give fault/alarm in case of high/low voltage at the input terminals. I mean can the module protect itself from high/low voltages? Best regards
|
10/2/2014 7:16 PM | |
Posts: 87 Rating: (7) |
Hi Ali Alkarn. Yes, there is a protection for BLM (Basic Line Module). You can see this case in the attached file. There is a fault F30002 "DC link overvoltage". There is a fault F30003 "DC link undervoltage". The reference for these faults it is a parameter ''r0070[0]''. Hope this helps. Regards AttachmentVisio-fp_8760_05_eng.pdf (123 Downloads) |
This contribution was helpful to1 thankful Users |