Hello Gustavo, BASP LED On means that the PLC has to write to an adress that he doesn't find. As a matter a fact, the BASP inhibits all configured outputs. QVZ : is a time out on the inputs. It's already a long time ago that I'm confronted with these led's. Here is documentation : https://support.industry.siemens.com/cs/attachments/1085940/pa928ben.pdf?download=true What you can try : - Does your CPU run on empty program ? - Did you configure some I/O in DB1 and if so does it correspond with the physical settings ? - Does you configuration CP143 on S5 side and NetPro configuration on S7 side correspond according to mac adresses and IP adresses ? Regards, |
Last edited by: Jen_Moderator at: 8/24/2017 10:34:54 AMInserted right link. |
|
8/18/2017 3:58 PM | |
Joined: 10/7/2016 Last visit: 10/10/2023 Posts: 66 Rating: (1) |
Hello AutoGen, I solved, it was I/O problems. Thank for help |