11/25/2013 8:42 AM | |
Joined: 10/9/2007 Last visit: 10/8/2024 Posts: 1250 Rating: (115)
|
Hi John are you talking about Siprotec? Mike |
Energy Automation products: Sicam, Siprotec, Digsi |
|
11/25/2013 9:10 AM | |
Joined: 11/7/2012 Last visit: 8/28/2023 Posts: 67 Rating: (0) |
Hi Mike, Yes I am talking about 6MD66... |
11/27/2013 10:07 AM | |
Joined: 11/7/2012 Last visit: 8/28/2023 Posts: 67 Rating: (0) |
Dear Mike, I improve my CFC & Configuration as per your advices; Synch On works perfectly. But, the problem is Synch Override! When I use>Block 25-1& while>25-1 eff is enabled,Nocommandexecuts. I think>Block 25-1 compeletly block the commands for CB closing. Using>25-1 dirCO is not safe, I assume! For more clarification on what I've done in CFC, please find the attachment. And just be advisethe BCU firmware is 4.82. Thank you John Attachmentsynch.pdf (183 Downloads) |
12/2/2013 7:44 AM | |
Joined: 11/7/2012 Last visit: 8/28/2023 Posts: 67 Rating: (0) |
Hi Mike, Synch On is OK as it was. Synch Override is still not working. I think it's blocked somehow! As you said I use 2 synch group (Print screen of both group is attached). The new CFC chart is also attached, please have a look. I am working on it. If you come up with someting let me know.. Just be aware "Dead Line & Dead Bus" is removed from our condition for issue commands. Thanks AttachmentSynch2.pdf (172 Downloads) |