9/20/2007 4:18 PM | |
Joined: 4/24/2006 Last visit: 1/17/2025 Posts: 8807 Rating: (1173) |
Hello, Please try to perform an OS update, see following link: http://support.automation.siemens.com/WW/view/en/19701610 Have a look at point 5. So you must use the option Booting Best regards, Wizard |
This contribution was helpful to1 thankful Users |
11/10/2010 4:12 PM | |
Posts: 52 Rating: (4) |
I have exactly the same problem. Did anybody find a solution? |
11/10/2010 4:30 PM | |
Joined: 4/24/2006 Last visit: 1/17/2025 Posts: 8807 Rating: (1173)
|
Dear rigor, Please see following link: how do you do an operating system update (OS update) on operator panels? You should use the option "Reset to factory settings" Best regards, Wizard |
This contribution was helpful to2 thankful Users |
10/5/2020 10:22 AM | |
Joined: 8/3/2009 Last visit: 1/17/2025 Posts: 14593 Rating: (1818)
|
Hello Pandi Please follow the Link that wizard have posted a few times... how do you do an operating system update (OS update) on operator panels? -->>> you need a RS232/PPIMulti-MasterCable (6ES7 901-3CB30-0XA0) or a USB PPI-Multimaster Cable (6ES7 901-3DB30-0XA0). -> Only with this Cables you are able to do a Reset to factory settings!!!!!!!!!!!!!! Its the only way you can restore the Panel functionality. And it doesn´t matter which Image Version yyou have for Prosave because the main goal is to get the Panel work again. Then you can do a Project transfer with OS Upddate/Downgrade and then the right corresponding Image Version is sent to the Panel. Bye Murof |
If this Information really helps, you could use the Rate function |
|
This contribution was helpful to1 thankful Users |