9/18/2015 9:44 PM | |
Posts: 111 Rating: (1) |
I am using Siemens S7 300 PLC model 315 2PN/DP and it is communicating with Servo Motor through CU305 module and I am using Part # 1FK70423BK711RA0 Servo Motor with it but now I am changing the motor to Part # 1FK70423BK711RB0 to add brakes. Can Anybody tell me; Do I need to make any changes in the program for brake functions or Brakes will Automatically applied? Which software I need for above model of the software and which type of communication cable I need for this Motor? ------------------------------------------------------------------------------------------ |
Last edited by: CS Moderator at: 9/20/2015 11:51:49 PMNew subject after splitting |
|
9/22/2015 1:10 PM | |
Posts: 111 Rating: (1) |
I still need a solution for my last post. If anyone can help then it will be highly appreciated. |
9/23/2015 2:18 AM | |
Posts: 1529 Rating: (202) |
If you enable brake control, it works all by itself. See attached from the S110 Function Manual. |
This contribution was helpful to1 thankful Users |
9/28/2015 7:30 PM | |
Posts: 111 Rating: (1) |
i need a connection of brakes from CU305 PM340 to 1FK7 motor. I look at the connection in the attached drawings but can't understand the output coming from connector 1 & 2 is 24VDC or 120VAC if it is DC then why we are using external relay as mentioned in S110 manual because as per my understanding switching of the brake will be through a parameter P1215. AttachmentS110 brake (2).pdf (275 Downloads) |
12/21/2017 4:54 PM | |
Joined: 5/28/2015 Last visit: 3/18/2024 Posts: 23 Rating: (6) |
Check parameter p1351. |