7/27/2016 1:18 PM | |
Joined: 3/2/2007 Last visit: 1/10/2025 Posts: 966 Rating: (5) |
any ideas? thank you... |
... thank you ... |
|
8/1/2016 10:49 AM | |
Joined: 4/23/2015 Last visit: 6/12/2023 Posts: 168 Rating: (9) |
1. 12 kW was a mistake I meant 120kW - the peak power of your resistor, so you could type in 120kW*s 2. Actually this value is even higher because the resistor can stand huge short-time overloads. 120kW*s is a "pessimitic" value, which is surely enough for any application for providing guaranteed overload protection for you resistor, and I would use it if I have no further tech details, like in your case 3. If you put this value too small, then you could probably get the drive tripped with a trip message like "Braking resistor overload" or "overheated" or something like that, but actually the resistot stays cold or just warm. In this case you can increase this value in the draive parameter. This is like empirical approach. 4. To be exact this value is very much dependant of some external conditions, like ambient temperature, ambient air flow, and is given of course for definite ambient conditions. From this point of view it's very good to have reasonable margin for this value, i.e. to type in smaller values |
8/2/2016 10:07 AM | |
Joined: 3/2/2007 Last visit: 1/10/2025 Posts: 966 Rating: (5) |
to be safe, i have put the parameter value equal to half the competitor's, which will be 500 000 watt-second. now the machine is running ok. to be monitored. thanks |
... thank you ... |
|
This contribution was helpful to1 thankful Users |