Hello, Unfortunately your 1215 CPU have only 0-20mA analog output link too see HERE So solution will be to add to CPU analog module 6ES7 232-4HB32-0XB0 witch keep +- 10 V Or use your internal CPU analog output 0-20mA and connect to your DELTA to ACI contact wich read 4-20mA Or last solution put 500 Ohm resistor and 0-20mA will convert to 0-10V add attachement for DELTA analog inputs |
Last edited by: Mr.V at: 07/04/2022 10:33:38 |
|
7/5/2022 8:27 AM | |
Joined: 5/6/2010 Last visit: 4/25/2025 Posts: 2017 Rating:
|
Hello, you don't need a additional analog module for your PLC. You vcan also use a signal conditioner e.g. Signal conditioner - MINI MCR-2-I0-U-PT Signal conditioner - MINI MCR-SL-I-U-4 With this parts you can adapt ypur signal 0..20 mA to a signal 0..10 V. regards |