6/25/2009 8:15 AM | |
Posts: 103 Rating: (11) |
how are you all member in the forum , first I want to thank UMENCHO , dchartier, WIZARD for their replies in the forum . I have S5 serive in cement plant in very far away state , I finished modification in S5 software in my office . my client has PG & EPROM my problem is , I don't know what is the setting that I should adjust in the software & HW driver??? & what is the common problems that may be face me? because this is first time to deal with S5 !!! in the attachment you will find pictures of screen that I guess it has important role in the problem. Attachment1.zip (1058 Downloads) |
This contribution was helpful to3 thankful Users |
6/25/2009 9:32 AM | |
Joined: 4/24/2006 Last visit: 10/3/2024 Posts: 8744 Rating: (1168) |
Dear ahmedmae94, Here is a link to manual: http://support.automation.siemens.com/WW/view/en/9830806 See chapter 18.2 about Eprom handling. Because you are using a Siemens PG, you have Internal Eprommer. Prognumber is depending on used Eprom Be sure Eprom is empty If not you will have to erase it with UV light. Best regards, Wizard |
6/25/2009 3:39 PM | |
Posts: 103 Rating: (11) |
very very thanks WIZARD |