12/20/2017 2:10 PM | |
Joined: 12/13/2012 Last visit: 1/16/2019 Posts: 124 Rating:
|
Unfortunately, I´m not a Modbus expert, but I saw that there are no answers yet. Maybe the application guide will help ? Otherwise, I suggest to do a suppoer request : www.siemens.com/automation/support-request. AttachmentSmartLinx_ModbusTCP_IP_instruction_and_use.pdf (28 Downloads) |
Last edited by: Jen_Moderator at: 12/21/2017 12:54:03 PMAdded PDF as an attachment. |
|
1/8/2018 9:23 PM | |
Joined: 12/16/2010 Last visit: 8/3/2023 Posts: 9 Rating:
|
Hi DocIshi The BW500 has gone through a few hardware changes and FW changes over the past three years. The BW500's hardware was changed about two years ago when we added an isolated RS485 port to improve communications with a multidrop network. The FW was also changed to improve MODBUS communications, taking the timeout responce from 1100mS to around 400mS. We tested the BW500 with Kepserver @19200 to ensure that communicates ran without error for a period of 24 hours with the retries set to 1. What baud rate are you using and how many registers are you polling in one read? I hope this helps |
This contribution was helpful to
1 thankful Users |